The SLA (Service Level Agreement) widget calculates the percentage of time the acceptable service levels were maintained for resources or websites included in the widget. You can define the acceptable service levels in the widget’s configurations.

SLA widget

SLA Widget Calculations

The SLA widget calculation is the amount of time the individual resource or website met its acceptable service levels as compared to the amount of time covered by your SLA.

The SLA widget supports a maximum calculation time range of six months. If you select a time range that exceeds six months, the widget automatically adjusts the start date forward and calculates the SLA using the most recent six months.

This behavior applies to both predefined and custom time ranges. For example, if the selected range is 1 January 2026 through 31 December 2026, the widget adjusts the effective range to 1 July 2026 through 31 December 2026. The widget displays the restricted six-month range, and the SLA value is calculated using only that period.

Note: SLAs can include time periods that are not under consideration in their calculations. For example, regularly scheduled outages for updates or backups.

However, if you want your widget to display a single percentage that represents the overall SLA value for the websites or resources being monitored, there are additional calculations that take place, as shown in the following table:

Entity CalculatedDescriptionExample
Websites and ResourcesThe overall SLA summary value is calculated by averaging the percentage of time that acceptable service levels were maintained by the individual websites or resources.For example, an SLA widget is measuring the availability of the following four websites over a one-day period:

  • Website A: Unavailable from 08:00-09:00, 95.83% (23/24 hours)
  • Website B: Unavailable from 09:00-10:00; 95.83% (23/24 hours)
  • Website C: Unavailable; 100% (24/24 hours)
  • Website D: Unavailable from 08:30-09:30; 95.83% (23/24 hours)
The overall SLA summary value for websites A, B, C, and D is 96.87%, which is the average of the individual availabilities.
ResourcesYou measure the percentage of time in which all resources concurrently met their individual thresholds for acceptable service levels.For example, an SLA widget is measuring performance thresholds for the following four resources over a one-day period:
  • Resource A: Fell below a defined threshold of an acceptable service level from 08:00-09:00
  • Resource B: Fell below a defined threshold of an acceptable service level from 09:00-10:00
  • Resource C: Met an acceptable service level threshold all day
  • Resource D: Fell below a defined threshold of an acceptable service level from 08:30-09:30
Based on these metrics, the total window of time in which at least one resource was performing at a subpar level was from 08:00-10:00, which evaluates to an overall SLA value of 91.67%. If these four resources were calculated using the average approach of the other calculation method, the overall SLA value would be 96.87%.

Configuring an SLA Widget for Resources

  1. In LogicMonitor, navigate to Dashboards, select a current Dashboard or create new, and then add an Advanced Metrics widget.
    SLA widget
    For more information, see Dashboard Creation.
    For more information, see Widget Creation.
  2. Configure the Basic Information settings.
    Basic Information settings
    For more information, see Configuring Standard Widget Settings.
  3. Select whether to configure a predefined time range or custom time range for the widget by doing the following:
    • To configure a predefined time range for the widget, select Predefined time range and then choose a time range option.
      Predefined time range settings
    • To configure a custom time range for the widget, select Custom time range and then configure the time range settings.
      Custom time range settings

Note: SLA widgets support a maximum time range of six months. If you select a time range longer than six months, the automatically widget calculates and displays the SLA using the most recent six months.

  1. To add a widget-level filter, select Add iconfrom the Filter by field in the Resource SLA Options section, and do the following:
    1. Type a property in the Search records field, or select a property from the list of properties displayed.
      LogicMonitor displays applicable properties as you type.
      Widget-level filter settings

Note: Only resource properties are supported for this filter.

  1. Type a value for the property in the Search records field, or select a value for the property from the list of values displayed for the property.
    LogicMonitor displays applicable values as you type.
  2. Select whether to include or exclude the value in the filter.
    You can select anywhere outside of the filter configuration settings to view the dashboard with the configured filter.
  3. Toggle Allow the Widget level filters to override the dashboard filters switch. Toggling this switch enables individual widgets to display data independently of the dashboard’s global filter settings.
    You can repeat this process to add a widget-level filter for as many resource or instance properties as needed.
  1. In the SLA Options section, select Resource.
  2. In the SLA Period section, do the following to configure the days and time range for the SLA period:
    Note: These settings reflect the time range of your SLA sand not the time range of the widget.
    1. Select the days you want to include in the SLA period.
      All days are selected by default.
    2. Configure the time range for the SLA period by doing one of the following:
      • To span the SLA over all 2 hours of the selected days, select All Day.
      • To span the SLA over partial days select Custom Time Range, and then configure the range to apply to each day that the SLA spans.
        Custom Time Range settings for SLA widget
  3. From the Time Zone dropdown, select the applicable time zone.
  4. From the Behavior When No Data Is Selected dropdown, select one of the following to establish the impact that no reported data has on the SLA calculation:
    • To consider unmonitored time in the SLA calculations, select “Subtract from total possible time.”
    • To consider unmonitored time as a violation against your SLA, select “Subtract from uptime.”
    • To consider unmonitored time as meeting SLA requirements, select “Add to uptime.”
    • To consider time delay or receiving data, select “Collector delay with no data.”
      For this option, a delay is considered when the data comes within the set poll interval delay time. However, if the data comes after the set poll interval delay time, it will be considered as system down.
      In addition, if you change the set poll interval time, the SLA calculation might be affected, and an incorrect SLA is displayed.
  5. From the Metrics Display Behavior dropdown, select one of the following to configure how the metrics display in the widget:
    Note: The value that is calculated is determined using the method selected in the Calculation Method field.
    • To display a single SLA summary value for all resources monitored, select “Aggregate SLA metrics and display one number.”
    • To display up to four individual SLA metrics (as saved in the Datapoint table) in its display quadrants, select “Display up to four SLA metrics.”
      If a metric has more than one resource associated with it, the resources are aggregated into one overall SLA number using the calculation method selected in the Calculation Method field.
    • To display up to 50 of the lowest performing SLA items per datapoint, select “Display up to 50 SLA metrics in table.”
  6. In the Bottom Label field, enter a bottom label to identify the resource this SLA is for in the widget.
    You can leverage tokens in this field.
    Resources only settings for SLA widget
  7. In the SLA Items settings, select Add Record, and then do the following:
    1. Add datapoints.
      For more information see Widget Datapoint Configurations.
    2. In the DataSource SLA Threshold section, configure the Datapoint value must be setting to determine the thresholds for this widget.
      You can use the Current global thresholds for reference.
      DataSource SLA Threshold settings
    3. To remove scheduled downtime (SDT) from the SLA calculations, toggle on Exclude SDT Periods, and then select one of the following:
      Note: These thresholds are not connected to the alert thresholds, so having a number show up as a color (even though they are the same colors) does not result in LogicMonitor alerting you.
      • To exclude only SDT set at the resource level from the SLA calculation, select Resource.
        Any SDT set only at the group level is considered an outage and counts as downtime for the SLA.
      • To exclude only SDT set at the group level from the SLA calculation, select Resource Group.
    4. (Applies to the “Display up to 50 SLA metrics in table” option in the Metrics Display Behavior dropdown only) In the Bottom Label field, enter a bottom label to identify this datapoint.
    5. Select Apply.
      You can add as many datapoints as needed.
  8. In the Calculation Method section, select one of the following:
    • To measure the percentage of time that resources concurrently met their individual thresholds for acceptable service levels, select Percent of all resources available.
    • To average the percentage of time that acceptable service levels are maintained by the individual resources, select Average of all SLA metrics.
  9. In the Display Settings section, configure the following for how you want the widget to display on your Dashboard:
    1. (Applies to the “Display up to 50 SLA metrics in table” option in the Metrics Display Behavior dropdown only) From the Quantity to Display dropdown, select how many results you want displayed.
      Note: The widget supports a maximum of 50 total items.
    2. To enable up to three varying colors to display depending on the current SLA value, toggle on Change Number Color According To Thresholds.
      For example, you can configure your SLA widget to display any SLA values lower than 97% in red. This is an excellent way to provide at-a-glance indicators for the general wellbeing of the resources or websites being monitored.

      Note: These thresholds are not connected to the alert thresholds, so having a number show up as a color (even though they are the same colors) does not result in LogicMonitor alerting you.
    3. (Applies to the “Display up to 50 SLA metrics in table” option in the Metrics Display Behavior dropdown only) To display the thresholds defined as percentage bars, toggle on Show percentage bar.
  10. Configure the Widget Color Schema settings.
    For more information, see Configuring Standard Widget Settings.
  11. Select Save.

Configuring an SLA Widget for Websites

  1. In LogicMonitor, navigate to Dashboards, select a current Dashboard or create new, and then add an Advanced Metrics widget.
    SLA widget
    For more information, see Dashboard Creation.
    For more information, see Widget Creation.
  2. Configure the Basic Information settings.
    Basic Information settings
    For more information, see Configuring Standard Widget Settings.
  3. Select whether to configure a predefined time range or custom time range for the widget by doing the following:
    • To configure a predefined time range for the widget, select Predefined time range and then choose a time range option.
      Predefined time range settings
    • To configure a custom time range for the widget, select Custom time range and then configure the time range settings.
      Custom time range settings

Note: SLA widgets support a maximum time range of six months. If you select a time range longer than six months, the widget uses and displays a six-month time range.

  1. To add a widget-level filter, select Add iconfrom the Filter by field in the Resource SLA Options section, and do the following:
    1. Type a property in the Search records field, or select a property from the list of properties displayed.
      LogicMonitor displays applicable properties as you type.
      Widget-level filter settings

Note: At least one resource property must be added before you can add an instance property.

  1. Type a value for the property in the Search records field, or select a value for the property from the list of values displayed for the property.
    LogicMonitor displays applicable values as you type.
  2. Select whether to include or exclude the value in the filter.
    You can select anywhere outside of the filter configuration settings to view the dashboard with the configured filter.
  3. Toggle Allow the Widget level filters to override the dashboard filters switch. Toggling this switch enables individual widgets to display data independently of the dashboard’s global filter settings.
    You can repeat this process to add a widget-level filter for as many resource or instance properties as needed.
  1. In the SLA Options section, select Website.
  2. In the SLA Period section, do the following to configure the days and time range for the SLA period:
    Note: These settings reflect the time range of your SLA sand not the time range of the widget.
    1. Select the days you want to include in the SLA period.
      All days are selected by default.
    2. Configure the time range for the SLA period by doing one of the following:
      • To span the SLA over all 2 hours of the selected days, select All Day.
      • To span the SLA over partial days select Custom Time Range, and then configure the range to apply to each day that the SLA spans.
        Custom Time Range settings for SLA widget
  3. From the Time Zone dropdown, select the applicable time zone.
  4. In the SLA Items settings, select Add Record, and then do the following:
    1. In the Website Group Name field, enter a website group name and select it from the results list or enter a * glob expression to select all website groups.
    2. In the Website Name field, enter a name of a website within the group you selected and select it from the results or enter a * glob expression to select all websites within the selected website group.
    3. To remove the scheduled downtime (SDT) from the SLA calculations, toggle on Exclude SDT Periods.
      SLA Items settings for websites
    4. Select Apply.
      You can add as many website datapoints as needed.
  5. In the Display Settings section, enable up to three varying colors to display depending on the current SLA value, toggle on Change Number Color According To Thresholds.
    For example, you can configure your SLA widget to display any SLA values lower than 97% in red. This is an excellent way to provide at-a-glance indicators for the general wellbeing of the resources or websites being monitored.

Note: These thresholds are not connected to the alert thresholds, so having a number show up as a color (even though they are the same colors) does not result in LogicMonitor alerting you.

  1. Configure the Widget Color Schema settings.
    For more information, see Configuring Standard Widget Settings.
  2. Select Save.